Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is phase voltage and line voltage? in line voltage how
415v is obtained?

Answer Posted / l a waygood

Let's get the terminology correct to start with.

The conductors that connect the load to the supply are LINES (or 'line conductors', NOT 'phases'! Which is why the voltages measured between them are called 'line voltages'.

PHASES are not conductors, but the connections, such as individual loads (or the windings of an alternator or transformer) between line conductors, or between a line conductor and the neutral.

So 'phase voltages' are measured between lines (in the case of a three-wire system) or between a line and a neutral (in the case of a four-wire system).

So we measure line voltages BETWEEN lines, and we measure phase voltages ACROSS phases.

Is This Answer Correct ?    8 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

i karmveer bharti persuing b.tech . plz send me syllabus and name of reference books. for preparation of section eng.

2184


a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5

1749


11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??

1651


DEFINE BREAKING CAPACITY OF BUSBAR & HOW IT IS CALCULATED?

5288


Give the expression for the frequency of oscillations in an op-amp sine wave oscillator?

1159


Please define ohm’s law for a.c (alternating current)?

1134


in dc suppy frequency is zero why? if dc frequency is zero how to exist dc transients and ac transients

2226


What is the necessary condition for stability.

1259


Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?

1784


What is difference between Over Current & Earth Fault protection?

2489


what work will do diffrential realay DG set

2965


Why choke coil is connected in series with starter in tubelight??why starter is connected in parallel to tubelight??

3435


dg earth connect only in the amf panel or not why

2144


how we findout a ignater is faulty or not?

2161


How to do cable earhing? whether by grounding Armour to ground or by running extra G.I wire along with cable? which one is preferred mostly amoung them? If the second one is more preferable how many GI wires to be run along with cable (1 or 2)?

2204