Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

Answer Posted / carl_ellis

Yes, V=IR, but that happens because the transmitter
functions as a transistor, varying its resistance in order
to regulate the loop current.

It is expected that the power supply voltage remains constant.

The transmitter acts as a transistor and regulates the loop
current as long as there is sufficient power supply voltage
to drive the current through the loop resistance (ohms law).
If the power supply voltage is not adequate, the loop
current will be limited to something less than a full 20mA
and in some cases the transmitter power-cycles itself and
starts through repeated initializations, trying to drive
current, but failing to do so.

Changing the power supply voltage will not change the loop
current as long as the power supply voltage change is above
the minimum needed, because that is the design
intent/purpose of 2 wire loop transmitters: to regulate the
loop current to match the process variable the transmitter
is measuring. Any excessive power supply voltage is
'dropped' in the transmitter in order to regulate the loop
current.

Every 2 wire loop powered transmitter has either an equation
for calculating the voltage required for a given loop load
resistance or a graph called a 'load line' that shows
voltage versus loop resistance. The minimum required
voltage to light up the transmitter is called "lift-off"
voltage, which is the minimum required when a power supply
is directly connected to the transmitter, like on the shop
bench, with no load; no analog input, no appreciable wire
resistance.

A typical 24Vdc power supply will drive 500 ohms of loop
resistance with most 2 wire transmitters.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How an rtd work, and what volts/current goes to a rtd to measure the resistance?

1268


What do you know about gail?

2467


How to calibrate an pressure gauge with yantrika test bench?

2900


how can leve transmetter calibate in feild .and also put cv and flow plz .....

2234


What is the difference between uv and ir scanners? and what is the workig principle of both

2359


2. What is ultrasonic flowmeter?

5069


I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.

1784


Describe how to use megger to measure the earth resistance and insulation resistance

2225


What are different types of cable?

1087


How to calibrate RC Feeder system in thermal power station?,If any instrument available to calibrate it,ple inform me. make:stock,

3166


State bernoulli’s application.

1136


What is force balance principle?

1155


Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?

10834


why we take %i0.0 as input for twido plc

2163


Questions on flow meters,few questions on HART protocol,

1983