Is it possible to connect a dYN1 transformer in
parallel with a YNd11 transformer.
Answer Posted / pramit dutta
according to condition of paralleling of two or more 3 phase transformer banks ,the phase shift between primary and secondary voltages must be same. it follows that all transformers in same main group can be connected in parallel.
| Is This Answer Correct ? | 9 Yes | 0 No |
Post New Answer View All Answers
what is W.T?specify the acceptable range?
Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?
what is difference between elr and R eartl realy.
Describe the control mechanism of missile launcher???
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
what is electrical machines
how we decide the require size is this for a known current at fuu load?
How npn and pnp transistor works
How to discuss the phase shift of transformer considering open delta?
Explain in details how you would react to an unexpected incident when your supervisor or manager is not around to give instructions?
why generator efficiency is more in swinburnes test?
why on delay timer used for fully automatic star delta starter?
can u tell me the promotion from oiller to enginer
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?