What should be ideal IR value for 11kV, un earthed, 1 MW
motor?

Answer Posted / sunny saini

ANYONE MUST FOLLOW THAT THE LEAKAGE CURRENT MUST NOT
GREATER THAN 1ma FROM PHASE TO GROUND.
SO
IR (MIN)= 11000/.0001=11MOHMS

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what happen if the load connected to the induction motor is taken away? the same question for synchoronous generator in synch i think that the the exitation voltage will appear on the terminal only if so plz answer me

1545


sir i applied for hpcl(electrical).i want to know from which subjects most of the technical que will b asked.and pattern of the written test.pls help me

1479


in indoor type circuit breakers why only the corner breaker trips specially during cold season. What is the reason.

1449


What do you understand by oldham's coupling ?

654


what is class of SPD and dittels of all class ?

1581






why different series of vfds (like allenbradley)are used in industry ?

1828


what is the calculation method to design core and winding of a 200kva 3phase distribution transformer?

1940


A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.

1716


is that any software calculator to calculate the size of cable

1870


What is Anemometer used to measure?

685


What is the formula to calculate a three phase alternator

1790


how to set the time in digital timer ?

1565


What will happen if the d.c. Shunt motor opened accidentally running on no-load has its shunt field winding?

895


What is different between resistance grounding system and resistance earthing system?

682


I have been using an 600VA with 0.6 p.f UPS with my desktop which has 450W power supply unit. Can anyone explain how can this happen . Because the output of the UPS is 360W (600*0.6) (<450W)

1677