I know the Capacitor value- 12.5KVAR, voltage 440V gas
filled, then what is the formula for calculate the
microfarad value for this 12.5KVAR capacitor
Answer Posted / 7anoter4
Explanation:
Q=Reactive Power in VAR
U-voltage at capacitor terminals[single phase]in Volt
frq=frequency[50 or 60 HZ=cycles/second]
Q=U^2/Xcap Xcap=Capacity reactance [in ohms]=1/(w*Cap)
w=2*pi*frequency
Then Q=U^2*w*Cap or Cap=10^9*Q/(U^2*2*pi*frequency) if Q
is in kVAR and capacity in microFarad.
If U is the line-to-line voltage the same formula is good
for three-phases in Y but Q=3*U^2/Xcap for delta connection.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
How to calculate VCB rating for 33KV ,25 MW Power line?
how to estimate wiring ins roughing ins. and boxes
Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?
What is warm / cold start of HT motors. How many warm start & cold start are possible in a day?
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
How can we calculate strength of copper hich is supplying electric power to heater and in it hold the heater also and what r all types of forces which is acting on it...
How does an oscillator differ from an amplifier?
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
What is I to C?
how can we select the type of wire.what factors we have to look on it , do we have some formula to calculate it. please guide me on it
which model T or pie model is prefarable in power syatem
substation+ plc system
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
What is the difference between the impedance percent and impedance voltage ?
Give the expression for the frequency of oscillations in an op-amp sine wave oscillator?