How to Select transformer for 100HP
motor plz... With calculation
Answer Posted / ilyas
For a 100HP motor which equals to 74.58KW a transformer of
max capacity of 63kVA could be used...
As the maximum load at 0.8pf here would be equal to 59.664KW.
| Is This Answer Correct ? | 2 Yes | 3 No |
Post New Answer View All Answers
What are the reasons for the parallel operation of transformers?
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
Pl. brief about break-down maintenance of machine tool.
What is process of anneling transformer core
Vibromotor 252MV 1/4HP2P..what is mean by 252MV?
how can we make cable shedule for controll wiring ? which details must be required for it.?
How can you sized or estimate the ligthning arrester current rating?
What are the criteria shall be considers for sizing Fuse and MCB? If the rated current is 10Amps what should be the fuse size / MCB Size?
What is the need of generator relay panel
What is advantages of VSCF wind electrical system?
why HT armoured cable does not glanding
how to calculate fuse rating for a motor
i want use the cable size 16cx4 core aluminium usege watts 240x2000w this cable size is correct?
What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer
what is the difference between 4pole & 6pole DC Motors & give advantage ?