Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what is the purpose of taking HV test in LT panel.

Answer Posted / karna

In LT Panel HV test we are conducting for checking the
insulation level of Busbars or components, and verifying
the Clearnace of Phase to phase or phase to Body.In fault
conditon Panel components are withstanding or not. HV test
applying voltage is 2.5KV for One Minute

Is This Answer Correct ?    6 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is thermal resistance of PVC Cable.

1751


Why can't we parallel the secondary circuits of two voltage transformers?

1435


How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.

2317


what is maxemo work permit procedure

2148


11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?

1923


I want d.g.set our company

1812


Is it possible to connect a safety device in to parallel?

2077


Don't you have similar question banks related to Oral Certification Examination conducted by Mercantile Marine Departments / Directorate of Shipping, Ministry of Shipping for Electro Technical Officer?

1617


What is the formulae of Megger value for a A.C.Motor

2811


I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.

2389


How to test Alternator stability test for REF relay

1429


HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?

2541


What are the uses of stepper motor?

1176


What is the classification of hydro projects based on installed capacity?

1132


why magnetising curve not start with zero voltage?

2238