What are the precautions to be taken before working on a
cable?
Answer Posted / sheikh
If cable is disconnected from both side then no any precaution
required but if cable connected from one or both sides then
before starting any work on cable discharge the residual
charge by connect every one lead of cable to earth momentary
and during the work cable should be remain short to earth
to avoid any possible electrical charge.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
how can see the ac indoor or out door ac which Tr
What are dependent sources?
What happens to a motor if it is connected in Delta connection
What is CCT (Correlated Color Temperature) ?
what is the role and fuction of automatic transfer switch in rotary ups
How 3 phase invertor works?
Can i replace Earth leakage relay to the faulty Earth Faulty Relay
What is the use of oil in transformers?
What is the Resposiblity of Electrical Utility Engineer
What do you mean by a phase angel of instrument transformer?
What is Servo Ventilated Motor?
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
why we use Test Terminal Block in 11 KV and 33 KV electrical panels.
what is meant by impedance & transient protection?
What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating