Distinguish between Earth & Neutral?

Answer Posted / sanjeet singh

Earth is a natural "0" reference point where voltage drop
becomes zero as there is almost zero resistance of the earth
due to which full voltage is built across; while the same
zero reference can be achieved artificially by making a
neutral point as in transformers.
But it may be noted that due to voltage unbalance, neutral
of the transformer may have some voltage and in the same way
due to bad earth resistance we may not get a perfect zero
reference from ground.
To overcome this problem, we can ground the neutral of a
transformer to the earth by making perfect earth pits; that
should necessarily be separate from general body earth mats.

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What are the different power system losses and how can it be eliminated?

1576


How to measure size of cable on a given load

1389


what is allowable ac mixing in dc

1547


What is the cut-off rate?

723


Define ampere

713






How to calculate the fuse rating depend upon the DC circuit?

2400


what is the major difference between LIBBP & HIBBP.. which one is most preferable..

2030


what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.

2985


Z transform is use when system is not a) converges b) diverges

1186


What are motor generator sets and explain the different ways the motor generator set can be used ?

719


what is gas turbine intercooling ?

1616


How do I calculate a WTI CT ofa 1250kVA 6600/400V transformer

1315


What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.

1634


What type of core material is used for metering C.T and protection C.T???

1696


What the main causes of transient interruptions on Over-Head Distribution Lines?

1595