What is difference between MCB,MCCB,ELCB and RCCB?
Brief description and why RCCB is costly?
Answer Posted / dixit
mcb
is a circuit protecting device which has a definite current rating which protects selective rating of the MCB which we choose.
MCCB
is also a circuit protective device we can change minimum to maxium value of current rating which can select .
ELCB
which sens the leakage current if any in the circuit,and trip the circuit immediatly
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
Is a d.c.compound motor is use as a booster? how?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
We have Diesel generator of 200KW. fuel consumption is always same,even connected light load or full load. Is it right?
what is meant by impedance & transient protection?
how to calculate percentage impedence at 75 deg C at normal tap
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to confirm its base capacity?
define hysteresis loss, eddy current loss and windage loss
What is ideal IR values for ground and neutral.
How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?
how to calculate the capacitor to maintain power factor?
What is the difference between voltages or potential difference? And what are they?
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
What are the difference between normal application Transformer and Solar application Transformer?
How many kinds of E.L.C.B and how to work E.L.C.B
What is the general power consumption rating of CPU CRT type and Flat type, Monitor,Printer, projector, Scanner?