what is the difference between id fans and fd
fans
Answer Posted / m talha aziz(cap)
In a balanced draft boiler you actually have both F.d fan and I.D fan.
1. I.D stands for Induced draft Fan whereas F.D stands for Force Draft fan.
2. ID fan(Induced Draft Fan)basically pulls out flue gas from
the furnace of boiler. FD fan(Forced Draft Fan)supplies the
required air into the furnace for combustion of fuel.
3. It is located between dust precipitators(ESPs) and Chimney. Obviously it handles hot air/dust. F.D handles air at normal temperature. The capacity/power rating of ID fan will be more than that of FD fan.
| Is This Answer Correct ? | 97 Yes | 16 No |
Post New Answer View All Answers
What is the main use of rotary phase converter ?
Define average demand?
Anybody tell me about modbus hex address of l&t trivector meter er300p??I want to read voltage,current,kwh etc via rs485...If anybody have a manual then send on my mail..Brijeshmodi18@gmail.Com
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
How much voltage we need to apply in 33kv cable during hipot test of cable
block diagram of 2 ups system connected in parallel mode?
what is the use of power transformer in GSS.
What is superposition theorem?
how to extend relay operating timing in 24V dc relay card (without using Timer )
What does the kvar means?
define displacement & magnitude ?
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
can we use ZNyn11 transformer instead of Dyn11 transformer in distribution for effectively eliminating harmonics from the industrial loads.
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
Zone of protection and tripping scheme of arc protection relay.