Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?

Answer Posted / ashish

A = Appearing as a first letter denotes Aluminium Conductor.

Y = PVC Insulation or PVC Sheath depending on the position in which it appears.

2X = 2-X (Cross-linked Polyethylene) Insulation.

W = Round Steel Wire Armouring.

WW = Double Round Steel Wire Armouring.

F = Formed Steel Wire (Strip) Armouring.

FF = Double Formed Steel Wire (Strip) Armouring.

C = Metallic Screening (Usually of Copper).

CE = Metallic Screening (usually of Copper) over each individual core.

Wa = Aluminium Round Wire & Aluminium Formed Wire (Strip) Armouring
b) Type Designations :
AYY Aluminium Conductor, PVC Insulated, PVC Outer Sheathed.

AYWY Aluminium Conductor, PVC Insulated, Galvanised Round Steel Wire Armoured and PVC Outer Sheathed.

AYFY Aluminium Conductor, PVC Insulated, Galvanised Flat Steel Wire (Strip) Armoured and PVC Outer Sheathed Cable.

AYCY Aluminium Conductor, PVC Insulated, Metallic Screened and PVC Outer Sheathed.

A2XCY Aluminium Conductor, XLPE Insulated, Metallic Screened and PVC Outer Sheathed.

AYCEFY Aluminium Conductor, PVC Insulated, individual core metallic screened, Flat steel Wire (strip) Armoured and PVC Outer Sheathed.

A2XCEFY Aluminium Conductor, XLPE Insulated, individual cores metallic screened, Flat Steel Wire (Strip) Armoured and PVC Outer Sheathed.

Is This Answer Correct ?    20 Yes 5 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to carried out tan delta test in 11 KV alternator ?

3128


I have doubt that the supply HZ (very low or high than rated ) may affect the power factor. is it true. ?

1728


How to calculate multiplying factor of dc energy meter

1713


role of europe union in UK safety legistlation (electrical safety)

1814


What is primary and backup protection?

1210


How to calculate per unit impedance of transformer?

2274


I need the list of Universities who have summer intake for BS degree in Electrical Engineering.?

2142


In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?

2337


Is better to supply the voltage for static exciter from the auxiliary power source or from the SG terminals? And why?

2001


What is the effect on 3phase induction motor if current setting knob of DOL kept at minimum current?

3808


If i am running of spindle at 2000rpm ,but How to spindle stop at the second I am resetting the machine in CNC machines

1682


TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2

2440


What is Fire Panel ? How it works ?

2120


what is level 2 automation?

3203


how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???

2083