What is the criteria in selecting Air circuit breaker(ACB) &
Moulded case circuit breaker(MCCB) for a particular range?

Answer Posted / e.r k.k dash

Suppose there is 750 kva transformer.then acb can choosen by following foamula=kva*1.35=amp
750*1.35=1012.50 amp
So next higher range is chossen.that is 1250 4 pole with high breaking capacity.

Is This Answer Correct ?    1 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV

1602


what is ratio of copper wire size and current ?

1373


why in a swquence network representation, the negetive sequence generated voltage is taken as zero?

1513


how electical engineer is related to apsrtc (general) post? if they ask a question in interview as why did u choose this job what shd be answer

1647


What products have you designed which have entered high volume production?

1589






what id a dry type transformers and its function ?

1350


What is the form name of 'c' license, I want to download in web

1410


what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.

5019


DEFINE BREAKING CAPACITY OF BUSBAR & HOW IT IS CALCULATED?

4792


PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F

1789


What is inrush current? how can calculateit? what is the affect of it?

1547


What are the temperature elements?

721


How servo stabilizer works.

1642


In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?

1891


I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.

986