1 Ton = ? amperes & power.
How much power 1.5 TON split AC consumes in an hour at 17
C , 26 C & 28 C (thermostat' temperature).
Answer Posted / iqbal
Runing amperes of 1.5 ton split AC = 7 Amperes
Voltage =220
VA = 220 x 7 = 1.54 va
W = VA x Power factor
= 1.54 x .9 = 1386 watts.
| Is This Answer Correct ? | 193 Yes | 55 No |
Post New Answer View All Answers
What is the phase relationship between the primary and secondary voltages of a transformer?
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?
What kinds of decision are made about CT from it's Knee point(voltage & current)?
When the relative speed between the magnetic fields of stator and rotor does is zero under steady state operation?
What is mason's gain formula?
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?
Air refrigeration cycle works on the
Explain the operation carried out in thermal power stations?
Why computer humming sound occurred in ht transmission line?
How to calculate cable size by using load.?? Any formula...
what is the difference between general inverter and solor inverter clerly explain plz
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr
How are load losses and no-load losses measured at site in a DG set?