what is necessity of using isolation transformer?
Answer Posted / venkat
what written in the above answer is correct but exactly
isolation transformer acts as magnetic connection between
source and load but not physically or electrically connected
so that it separate source and load in order to protect load
from high currents in fault conditions
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
hi frds, i m electrical engineer.can i get cdr for electrical engineer if u have then send me on my mail id its jayesh_ee88@yahoo.com.please help me frds
what will happen if multimeter(selector switch at DC voltage) and terminal at current is connected to DC supply?
In Power cable specification what is U0/U and Um.
what ispositive, negative, zero sequence impedence?
Which power will flow first if we switch on a motor Active or Reactive? How?
A ii kv 1200 A Breaker combination fixed in a cubicle. How many ampere Fuse is required? If fuse is not using, Why?
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
Safety of on line ups
Igfet is a
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
tan delta equation test on alternators
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
sir i have a car stereo system and there is jack on him so can u tell me a way to find out their power terminals on the jack or on the circuit board"
please give some hindalco placement papers for written exam
What should be the amps for a MV fuses for transformer 630kVA 20(10)/0.4 kV