how the length effects the ampacity of the cable? if a cable
is carrying a current of 100A for 50m length then what will
the effect on current if we double the length?
Answer Posted / murali
R=pL/A. So if u increase d length, then current will reduce...
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
While testing LA mast,What are the parameter limits ?
Explain cmrr?
how u measure/calculate renge of capacitor,capacitor has no any rating tag.what is the theory of measure of capacitons.
What is contract demand in solar system?
which book to refer in electrical engineering for iocl exam & which book for general english.
when qty of cable being purchased is not sufficient according to the standard,what should the inspector do to ensure its quality according to the standard?
how give earthing conection to household equipment?
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
In EB metering we face problem kva jump even in no load condition.can any one help to control this
in a simple IDMT relay we use neutral point of ct for earth fault then what is the requirement of neutral ct and cbct?
role of europe union in UK safety legistlation (electrical safety)
Why cables and busbar both needed in LT Panels?
The synchronous machine excitation system explain