How to calculate Busbar Thickness for Different type of
HT/LT panels

Answer Posted / sudhakar g

Basically we can consider busbar size according to incoming
of the breaker in the panel
Example:
63A incomer of a panel we can go for AL 25x3mm bcoz it will
carry current up to 65A

Is This Answer Correct ?    7 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the minimum requirement gigaohms for the insulation test using 5kv in 300mm xlpe cable

1533


Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.

1195


IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?

1977


How to calculate Voltage regulation of 22 KV Over head Line.

1200


how does high earth to neutral voltage affects electronic circuit?

1299






1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai

1394


how to know the diffrential relay setting of 06mva step- down (delta-star)transformer?

1535


How to measure current and voltage in an ELV circuit

3620


why swinburnes test cannot be performed on series machines?explain

1840


What is NGR . What is the purpose of 10 sec ,60 sec rating of NGR.

1258


if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm

1708


what type of earthing do for dry fissure rock?

2042


substation+ plc system

1634


If there are two transformer having rating of 2.5mva, 6.6kv/440v(satr-star),and the load is 600kw then what is better to maintain less losses in transformer having both transformer in parellel or only single transformer connected to load? Please give calculated answer

2277


What is MS-EXCELL?

1667