What is mean CT Saturation? How to calculate?
Answer Posted / raseelrasheed
SATURATION POINT CAN FIND USING OPEN CIRCUIT CHARACTERISTIC
TEST WITH HELP OF SECONDARY INJECTION KIT,
at first keep the primary and secondary of ct get opened
and connect the kit to secondary of ct,measure and note the
voltage and current and plot the relation graph,
we can see saturation at a point where 10% increase in
voltage causes 50% rise in current.this point is known as
knee point of saturation.
it can also find automatically using modern test kits like
omicron ct analyser etc
hope my answer helpful for u
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
why all the feeders are designed in a particular manner ... is there any reason for that???
difference between high and low impedance BUS BAR relay??
What is the principal of motor?
what is your majour contributions in your present job
What is the formula for selecting the cabels according to load? How to calculate what sq.mm cabel to be used?
physical identification of HT & LT panel
Why can't we parallel the secondary circuits of two voltage transformers?
what is mean by restructuring power system?
Differentiate between digital phase converter and ordinary phase converter.
Is any generator is developed which is operated with out diesal or other expensive source?
Define maximum demand?
How many types of electrical earthing are there?
how we can calculate power factor in single phase & three phase ?thank u
salam&hi, i need to know about how can i calculate an enough current for the new building before i submit it to the suppliers