Answer Posted / arvind kumar
Grid failure occurs due to grid disturbance. The grid
disturbance means tripping of one or more grid element like
transmission line, transformer, static var compensator etc
resulting in total failure of power supply at the substation
or loss of integrity of the grid at the transmission level
of 220kv and above.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?
what is the current density of copper & alluminium.
why Lightening Arrester Probe sharp at Top of telecom tower.
what is servo motor and how to work it.
What is the formula for selecting the cabels according to load? How to calculate what sq.mm cabel to be used?
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
TRANSFORMERS WITH DC SUPPLY
how to produsing geretor power
Name two low frequency oscillators?
where can the transformer having vector group Yny0 be used??
What is the Surge suppresor? Why using in a UDB's and How it works?
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
On what cycle does thermal power plant operate?
What is the difference between Encoder and Resolver?
what is upper impedance and lower impedance of a distance relay