What is oil temprature with A/T contacts in Transformer ?
Answer Posted / kc ng
Normally for transformer oil temperature >80deg = alarm.
if oil temperature >90deg = tripping of VCB.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what is fault level of power system ?
i m in need of current rating chart of heavy duty pvc/xlpe, cu/al cables. can somebody provide me? if yes, plz send me at ashish_patel111@yahoo.com
PIU how does work?
difference between high and low impedance BUS BAR relay??
WHY THREE PHESE SYSTEM VOLTAGE APPLIED IN 440 VOLT
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
difference between Ac and Dc mcb ????
how maney type tempereture measurement ?
How to calculate cable size in HT AND LT
what is the soft starter principle? how is connection diagram? what is the procedure for checking the connection?
why dc is used in control circuit for mv & hv switchgear instead of ac
What are the advantages of thermal power plant?
Role of active and reactive Power sharing in between two synchronized Generators, Droop Setting role ?
What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)