what is tertiary winding in transformer?What is its purpose?
Answer Posted / anil prajapati
TERTIARY WINDING
In Δ - Δ, Δ -λ and λ - Δ transformers all voltages are balanced and there is no floating of neutral. The floating of neutral is developed in the case λ- λ connection only. The transformers are sometimes constructed with three windings. The main windings are connected to form λ- λ connection and the third winding known as tertiary winding is used to make a closed Δ (Delta) connection to stabilize the neutrals of both primary and secondary circuits. The tertiary winding carries the third-harmonic currents and zero sequence currents (3I0).
HARMONICS are caused because of use of high flux densities in the core. If the core gets saturated during part of the sinusoidal wave, then secondary wave will be non-sinusoidal. This may be due to inadequate core area or characteristics of core material.
Harmonic currents result in:
1. Higher copper loss
2. Higher Core loss
3. More Magnetic Interference
4. Interference with Communication Systems.
Harmonic voltages result in:
1. Increased dielectric loss
2. Interference with communication systems and resonance between inductance of the winding and capacitance of transmission line.
Importance:
Importance of tertiary winding is given below:
1) To supply small additional load at a different voltage.
2) To supply phase compensating devices such as capacitor for power factor improvement which can work at different voltages.
3) In Delta connected tertiary winding reduces Zero sequence impedance and allow adequate current for operation of protective device in order to limit voltage imbalance which may be produced when in balance in load.
4) It indicate voltage in high voltage transformers.
5) It limits the fault current to flow.
| Is This Answer Correct ? | 10 Yes | 2 No |
Post New Answer View All Answers
how are reversing the direction of dc motor
george phenomenon of synchronous machine
Type of motor stater detail and working detail
how pt is using
Merits & Demarits of Oil circuit & Air circuit breakers ?
Name the component u would expect to find in a switchgear assembly?
In convertor can we use rectifier thyristor in place of invertor thyristor with explain.
How to calculate the Harmonics losses in terms of cost/unit.
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
If a shunt Dynamo has induced emf 100V and 0.4 ohm resistance and battery of accumulator of open circuit emf 110V and 0.5 Ohm resistance are in parallel what is common terminal potential difference?
what is the meaning of osr in transformer.
What is meant by control system?
what is relay what is protection & contact multiplying relays where it is used function in brief
Why does amplifier gain reduce?
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.