What is the difference between online ups and offline ups?
Answer Posted / roshan khadka
In on-line UPS,the batteries are always connected with
inverter so that there is no power transfer switch between
them and load is always connected through inverter whether
there is power supply or power on.
In off-line UPS, load is connected directly with ac source
in normal operation and battery charging will be there
during that period. But in case of power failure,load is
connected to the inverter via power transfer switch between
battery and inverter.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
Can XLPE/SWB/PVC (P3) 7C X 2.5mm2 be replaced by Can XLPE/SWB/PVC (P2) 7C X 2.5mm2??? P3 vs P2
what is interfacing in computer studies?
what is the difference between transformer,converter and transducer
why can the rotor of 3 phase slip ring induction motor not be a 2 phase rotor?
The screw thread commonly used for transmission of motion is one of the following types of threads
What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?
What is the power factor of an alternator at no load?
what is the profesional board for electrical engineer what is thepast and during construction for electrical engineering
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
why ss stablity limit is more transient stablity limit?
What is hipot test procedure?
and gate circuit diagram,amplifier circuit diagram
Can i use the B-curve MCB instead of C-curve MCB
What would be the size of wire used for 2 Ton of window A.C?
What does the term “voltage regulation” means?