1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
Answer Posted / kesavan b
ELCB - Earth Leakage Circuit Breaker
It will trips if any leakage in the elctric circuit
Current will depends upon which system you are using usually single or three phase
formula
Watts = VI Cos (Phi)
Watts = 1.732 * VI ( COS (phi) )
Is This Answer Correct ? | 489 Yes | 94 No |
Post New Answer View All Answers
What are the three major categories of error?
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
Why GRR starts from 60% of motor speed why not less than 60%?
What is ST and specify its range of voltage.
Do closed loops systems require manual input?
what is the difference between fault current ant short circuit current?
A 400 V, 50 Hz, Δ connected synchronous generator has a field reactance of 0.1 Ω and armature resistance of 0.015 Ω. At full load, the machine supplies 1200 A at 0.8 pf lagging. Under full-load conditions, the friction and windage losses are 40 KW and the core losses are 30 KW. What is the machine’s overall efficiency? Ignore any field circuit losses.
How many lightning arrestors to be installed on 50MX60MX10M building and is there any formular for that?
wat is meant by PX class in ct?
What is the role of Dedicated earthing in UPS System?
what is counter poise conductors
what are symmetrical and non symmetrical components in electrical installation.
What is lighting kitts.
How much inductance or resistance require as a starter in series with induction motor of specific capacity(e.g. 5 hp) ? What is formula for it ?