i have one source transformer with the capacity of 50KVA,
connected with two loads 10kw and second one is 15kw.. how
can i calculate first load in KVA and second one in KVA ..
because Kva rating, power factor rating of of transformer is
different from the load…
there must be some way to calculate load KVA rating and
power factor….
Answer Posted / mukhvir singh
for calculate from kw to kva
kva =kw/power factor
| Is This Answer Correct ? | 7 Yes | 2 No |
Post New Answer View All Answers
Either It Possible a dc Motor to Run On Ac Drive [ Ex : ACS 800 , Yaskawa F7 ] If it is Possible How Pls Inform Me dinesh_elect_eng@yahoo.com
which is the best institute for PLC,SCADA,DCS in hyderabad
circuit diagram of trip circuit supervision relay
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
How to calculate the fuse rating depend upon the DC circuit?
What is magneto on a gas generator. how it functions. its out put is d.c or a.c. how it can be checked for correct functioning
types of central Air conditioner plant?
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
what is the id1 & id2 setting in differential protection relay of CSPC?
why ss stablity limit is more transient stablity limit?
What is Surge Capacitor? Why it is use in Generator Circuit Breaker?
Can anybody inform me about the pattern of ECIL GET( Graduate Engineers Trainee) interview for Electrical students? Will there be HR round as well? I thought of preparing for 2 to 3 subjects thoroughly. Will it be sufficient? Please share your thoughts.
What is the general power consumption rating of CPU CRT type and Flat type, Monitor,Printer, projector, Scanner?
What is formula calculation size cable wire ?