Normally the
starter used to
reduce the
starting
current.but the
dol starter do not
it,so why we use
it?
Answer Posted / naresh
The name itself indicates direct online starters and these
starters will employed for low rating motors, because in
low rating motors the loaded torque is also low and
capacity of starting current will not be such high enough
to make severity, but the protection of motor at voltage
levels is important. DOL starter not only ensures on & off
but the magnetic opearting coil functions in proportion to
the rated voltage. at low voltage the magentic coil trips
down and at high voltages the coil gets damaged. here the
coil used is very sensitive to the voltage and hence it is
voltage protection device and the bi-metallic strip inside
starter makes it current protection device.where as mcb is
only current protection device.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what is the role and fuction of automatic transfer switch in rotary ups
can u tell me the promotion from oiller to enginer
How many VSC based HVDC are there in India and the world
What do you mean by cogeneration? What its working principle?
what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.
1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?
Can anybody tell abt concrete encased earthing or grounding?
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
DERIVE AN EXPREION FOR MAXIMUM POER TRANSMISSION, WHAT ARE ITS APPLICATIONS.
Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?
what is mean by parallel operation of permanent magnet generators
Why to keep capacitor bank off while generator running.
Why are the cores of large transformers built up of circular transactions ?
Explain what is use of lockout relay in ht voltage?
what is maxemo work permit procedure