Please tell me 1 ton = How many Kilowatt (Electrical)
Answer Posted / murali
1 TR refers 1 Ton(US) of refrigeration capacity. It is the
heat required to melt 1 Ton (907. 185 kg) per day of ice at
0 Deg C to water at 0 Deg C. This is basically the latent
heat of fusion of ice.
Latent heat of fusion of ice @ 0 deg C = 80 Kcals / kg
For melting 907.185 Kg ice / day, the heat required is
72575 Kcals / day or 3024 Kcals / hr or 3.516 KJ / sec.
Since 1 KJ / sec = 1 Kw, 3.516 KJ / sec = 3.516 Kw.
| Is This Answer Correct ? | 12 Yes | 7 No |
Post New Answer View All Answers
Efficient electrical earthing in hard rock area
What is bode plot?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING) I O (current operating)?
What is the method of estamating of cable, CB,MCB ?
Single line digram for 11 kV to distribution use go,la and do
tell me some type of questions throught which i can prepare for exam and do my best
1. transformer design formula ? 2. how to calculate the primary turns and secondry turns ? 3. core types ? 4. how to find the primary current and secondry current ? 5. how to calculate the stacking factor ? 6. range of fulx density ?
SUTIABLE FOR ohm's law super conductor
Hi, My plant daily consumption is calculated as 3.8MWH but my supplier has sanctioned an power of 2.6MW per day. how can i equal or distinguish this two factors
What are factors to be considered while we selecting the Core Balance Current Transformer for Earth fault protection
limitation of conductor height on ground when we consider EMC
application s to shunt coil
If you have an earth with pilecap then your resistance is really low. why and how?
How much costly in percentage wise is sandwich busduct costly than air insulated busduct of any rating?
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?