Whats the difference between three phase and single phase?
Answer Posted / amjith meeras
in three phase system we can use it in two modes one is delta connection and other is star connection,
in delta connection we will get only phase to phase voltage, in india its 415vtg its because of there was no neutral point in delta connection.
but in star connected it has one neutral point and 3phases in R-Y-B sequence so we will get phase to neutral voltage and phase to phase voltage from it.
for ex: the transformer primary was connected with 3phase 3core cable but its secondary side has one neutral and three phase it connected with 4core cable.
all machine other than motor wants neutral for it work.
Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
dg earth connect only in the amf panel or not why
is oil viscosity affect on motor current?
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
Describe the control mechanism of missile launcher???
What is the function of capacitor in electrical circuits?
Why only sinusoidal ac voltages are generated?why not triangular or sawtooth?
how is the connection of a 3 phase ct trivector meter done on a pole mounted transformer
why co incidence factor considered in transformer sizing?
What are the types of class b amplifier?
what is the need of starter in tube light and what type of starter is used in that?
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
How can calculate the rating of a servo stabilizer for given a specific load
which network topology offers the greatest level of tolerance?
How to calculate flow of water delivered by pump when pressure & size of pipe line is given