Whats the difference between three phase and single phase?
Answer Posted / amjith meeras
in three phase system we can use it in two modes one is delta connection and other is star connection,
in delta connection we will get only phase to phase voltage, in india its 415vtg its because of there was no neutral point in delta connection.
but in star connected it has one neutral point and 3phases in R-Y-B sequence so we will get phase to neutral voltage and phase to phase voltage from it.
for ex: the transformer primary was connected with 3phase 3core cable but its secondary side has one neutral and three phase it connected with 4core cable.
all machine other than motor wants neutral for it work.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
What is the capacity of the Fastners 12mm?
How dia computation perfomed in cold rolling mills .
aternator every parts and its working
what is stper motor
What are the reasons for the parallel operation of transformers?
list of tests to be carried out at manufacturers end while purchasing a step up transformer of 11kv to 66kv ,2MVa Capacity.
what is the calculation method to design core and winding of a 200kva 3phase distribution transformer?
what's producer of XLPE cable laying in undergroung
what is the max. acceptable leakage current in 33kv bus bar
What is earth system using on the floater TN-S or TT. Iam not sure and what ICCP
Starting Time of LT & HT Motor
How will you define capacitance?
What are the limitations of Kirchoff's laws?
Why open circuit test of transformers is conducted at rated voltage??Why not any other voltage??
How vfd saving power.