what is the difference between high impedance REF & REF,
same high impedance differential protection & differential
protection for Power transformer?
Answer Posted / guest
REF protection can be implemented as High Imp or Low imp.
In high imp scheme, the CT ratios needs to be same but in
low the CT ratios may be different. Same is for the
differential protection. If the CT ratios are same the high
imp scheme can be implemneted as in busbar differential
protection.Key advantage of High imp tech is its immunity
to CT saturation . Key adv of low imp is to use CT with
different ratios for differentail / REF schemes.
| Is This Answer Correct ? | 10 Yes | 0 No |
Post New Answer View All Answers
How to calulate Locked rotor amper(LRA) for compressor type motors?
why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?
which types of relay used in acb and vcb?
i am completed diploma in ece,and working in ht and lt lines.so is elligible diploma in ece for get electrical C Licence?plse give ur opinion?
how many load we can take for lighting
what is the difference between "Rotary bypass isolation switch and Normal bypass switch" pls share indepth techs?
how you configure motorvision relay (L&T make)from DCS
in science exhibition how lamp can blink when you clap near the lamp ? thank you
What must be the minimum distance maintained between 2 Generators as per International standards?
Explain the working of variable frequency transformer?
how to determine the inrush current of a transformer
Please explain me about Relay curves and their sources to read ?
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
How we calculate the Multiplying Factor of Kwh meter for 3 phase alternator.
what is meant by directional earth fault and non directional earth fault? describe both.