What is the distance between the EHV lines and also the
distance for earth ??

Answer Posted / k.prakashchandra

For EHV lines, the clearance above ground shall not be less
than 5.2mtr + 0.3mtr for every 33000 V or part thereof by
which the voltage of the line exceeds 33000 V, provided that
the minimum clearance along or across any street shall not
be less than 6.1mtr. And clearance between lines ( not
conductors),shall be not less than the height of the taller
tower above the ground.

Is This Answer Correct ?    14 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Y phase plates are used in transmission line??? what is there need???

2438


what is the saturation point of crgo lamination.

1643


What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?

2019


i want to run 11kv star connected motor in 6.6kv with delta connected throught inverter, is it possible?

1615


is it necessary to earth the rmu before cutting off the transformer winding?if yes why?

1475






why dc is used in control circuits for MV & LV switchgeras instead of ac

1475


What will be the voltage impact on secondary side of two transformers with different vector groups when both voltages are compared.

1520


how to maintain frenquncy with syncronising sub-station for distribution

1657


How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?

1155


What is the actual calculation for transformer short circuit test?.

1984


What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr

651


What is the effect of positive feedback on the stability of the systems?

643


what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network

3036


what is the total power generation in india?

1717


Why is remote backup preferred to local backup?

1496