Answer Posted / wareagle

Before you can answer this question you must knoiw the load
power factor.
KVAR amps = KVAR/(kv x 1.73) eg 600 kvar 400 volts
600/
(0.4 x 1.73 = 867 amps
To determine tha KVAR required you must know the existing PF
Then you determine what you want the new PF to be before
you can calculate the new PF.

Is This Answer Correct ?    1 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is meant by cold loop test in instrument

2128


What is the permissible limit of shaft voltage for 6.6 KV motors ? Why? Is there any standard is available?

2103


Importance of fault current in power transformers and how to monitor the same? How is it different from winding temperature?

1337


How does zener phenomenon differ from avalanche breakdown?

703


Why negative feedback is preferred in the control system?

867






What does bode plots shows?

681


ACCORDING TO IEC WHAT SHOULD BE THE MINIMUM HEIGHT OF G.I. STRUCTURE OF CT, PT, ISOLATOR, LA?

1621


Why High voltage are generate noise ?

960


how can we save enegry by using VFD for Resiprocating Air compressor which is having more unloading running hours

1800


What is transister define the transister ammiter ,base, colector.

1734


what is the differation bewreen kwh & fundamental kwh in electronic trivector meters

1776


What is the function of electron gun used in crt?

604


Parts of machine and their discription in details with suitable photo

1638


can any one tell in easy method for circulating current ??

1652


How to calculate the size of earth cable to earth the neutral of UPS ?

1419