Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

how to calculate the knee point voltage of current
transformer?

Answer Posted / manisand1


CT resistance = 1.8ohm,
Lead resistance = 4.0 ohm,
Starting current = 195*5/200 = 4.875 Amp
Starting voltage = 4.87(1.8+4)= 28.275 = 28.3 volts
This is to be set to 30Volt,

But please remember that knee voltage should be 60 volt
minimum.

For anymore clarification you can mail me to :-
manisand1@hotmail.com

Is This Answer Correct ?    1 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

why is the power generator connected as star earthed or star earthed through reactance and what its features ?

1690


I have iti elec, 1st aid, and 5 yrs experience in 7.5 mw power plant. Am i eligeble for 11kv license in telangana state..when, how to apply for that.?

2316


how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???

2176


what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm

5103


What is the relation between frequency and motor rpm?

1862


why three phase capacitor takes unbalanced current in capacitor bank?

1499


what does a k rating in a transformer means?

2516


What is the permissable nutral current of three phase system as per IS standards?

2118


What is the difference between the relay and the circuit breaker?

1129


Which power will flow first if we switch on a motor Active or Reactive? How?

5606


Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com

1940


Suppose a 3 phase, 2 pole, 440V induction motor is driving a flywheel of 600mm diameter, 150kg mass. By using v-belt and pulley, the speed is increased to 4500 RPM. What will be the effect on motor current?

1418


As a electrical engineer.. what are the basic norms should follow in transformer oil testing.. 1.What is the Electrode type? 2.How long time you will give for oil testing?

3643


What is Icu and Ics and what is difference b/w them. please tell me how to calculate a size of a copper bar for a system or a breaker... reply on... king.arish@gmail.com would be waiting for a logical answer.

2465


ITI r/tv trade APPLY (J.T.O VACANCEY) ALSO INCLUD AITT ELECTRONIC,WRITEEN XAM DONE 23.03.10 BUT NO RESPONCE WHY ANATHER ID gopal_gh007@rediffmail.com

3417