Answer Posted / sunny ponna
if we consider two conductors due to potential difference b/w them a violet glow is abserved around the conductor .
if the potential difference is further increased sparkover may happen . this phenomenon is named as corona
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
how mass curve differs from hydrograph.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What are the specifications for conducting earth leakage test as per IEC standard?
can i connect the two phases of scott connected transformer,if not why?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
1.why we are using blocks in withoutgaplightning arrester 2.why we ar using bushing in withoutgap lightning arrestor
What is the types of HT motor testing
What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?
What is q factor?
What is UPS and How do you maintain the UPS Maintenance? Brief Description on UPS maintenance.
What happen Grid EARTH plat got cut.
HOW TO CALCULATE THE VT SIZING?
what is the difference between "Rotary bypass isolation switch and Normal bypass switch" pls share indepth techs?
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
what do you mean by plant earthing system.