is it possible to flow currnet between earth and nutral
wire in a circuit???
Answer Posted / maddy.
Neutral is a circuit conductor (that carries current in normal operation), which is of a 2-wire circuit that is connected to the supply neutral point and earth ground is also to minimize the voltage difference between neutral and local earth ground. so the answer is yes, it will allow when the distribution is unbalanced.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
what shoud be strength and weakness to impress interviewer????????
why does make gain margin and phase margin on same plot.?
When calculating the speed of a rotor required for a particular frequency of synchronous generator we use the equation 60f/p Is this p is the number of pole pairs of rotor & do we consider the number of pole pairs in the stator is 1?
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
how hydrogen cooled alternator undergo maintanence ? that is hydrogen when come in contact with air can result into explosions .
Why space heater is required for each verical bus bar chamber? if one space heater is adequate or not for anti condensation?
what is the purpose that we use PLC system in power system
What is the significance of integral controller and derivative controller in a pid controller?
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
sir, I am from EEE branch.On feb 17 iam going to write an Exam for hindustan petrolium corporation Ltd.So plz send me the written exam pattern/Q's/interview questions.please mail to eee_dharmendra@yahoo.com
What is BusBar integrity test and how it is conducted?
Do you know what is dry-out test in x'mer
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.
What is tranformer differtial?