Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what do you mean by 1 ton in AC`s

Answer Posted / harshal v.p.o

1 tonne AC : it is the capacity of the compressor of Air
Conditioner,which can remove the heat generated in the
particular room,such that the amount of heat is equivalent
to melt a block of 1 tonne ice in 24 hours.

Latent heat of ice= 144 BTU
1 TR= 144 X 2000
= 288000 BTU/24

For 1 hour

If you dividing by 24
288000/24=12000BTU


Thank You
Harshal VPO
Tanur

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

is there any current and voltage drop on liquid resistance starter water/soda tank ?

1930


oil cooled transformer

2167


For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?

1853


what is meant by impedance & transient protection?

2061


how to calculate mf when meter and cTPT detail are given

1796


How out of step protection relay works?

2343


why fractional pitch winding generally used in alternators?

2894


Type of motor stater detail and working detail

1613


how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc

1793


If a air condition consume 2.50 to 3.00 amp then how much it will consume in watts if it is running 10 hours out of 24 hours????

1811


How the setting of the vector surge relay shall be calculated when the relay is to be used for Grid islanding application?

2203


How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???

2009


is oil viscosity affect on motor current?

1952


234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,

1971


how to find the torque of the single phase synchronous motor by doing an experiment

1888