what is the safety of ACB & VCB and how can this work and
how can the service the ACB & VCB parts name with picture
Answer Posted / rajesh verma
As you all knows that all circuit breakers can be called
as on off switch with some safety device ie ACB make and
break contact in air (one moving and one sliding) so it
called air circuit breaker for safety we use in ACB Under
voltage shunt trip closing unit. CBCT for tripping command
relay with over voltage earth fault etc for spring charge
we use motor charging mechanism. Same case with VCB
contacts makes in vacuum to minimize the arc during make
and break contact (one moving and one sliding) on high
voltage other function are same but according to the
voltage rating
| Is This Answer Correct ? | 121 Yes | 24 No |
Post New Answer View All Answers
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
IN 1000kva transformer where the oil and winding temperature sensors is connected
Why is the air gap between the pole pieces and the armature kept very small?
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
what is the eight bit unit?
Difference between shunt, PMG and AREP excitation. Which is the most reliable between PMG and AREP.
What is different bewteen low or high impedance busbar protection scheme
Why the efficiency of generator is more than motor in swinburne's test
which pump used in WTP explain the function of VFD how to dtermine capacitorbank of capacity one plant
Why generation voltage in thermal power plant is between 11kv to 33kv?
why co incidence factor considered in transformer sizing?
What is the name of the winding from which the supply is taken for load connections?
How can we select suitable capacity generator for three phase load (inductive load) and how to take study analysis in 3 three phase load system ?
what is per unit calculation?looking for simple and strong explanation thk u
Define availability (operational)?