you have a 2 tonne ac that operates for 2 hrs daily what will
be you monthly bill (this is complete question asked nothing
else was given)?
Answer Posted / sagar parekh
1 ton = 12000 btu/hr
= 12000*0.0003929
= 4.175 hp
= 3.5 kw
total hrs of month= 60 hr
kwh=3.5*60=210 units
suppose tariff is 3rupee per unit so final ans. is 630 rupee
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
How can we increase the capacity of Energy.?
tell me about eletrical contractor
Why does increasing the magnetic flux in the main field of a d.c motor cause the armature current to reduce??
exolain the star delta connection
Why it need to form a capcitor when it not been in use from three or two year. Plz describe it technically.
Please, if 1kw is equal to 1.25kva; how then do I know how many kva in 7.5kw?
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
What type interview questions ask in Electrical technicians
Determine the BTU size of an aircon for 20 sq metre room
What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.
What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
how can you size an automatic voltage regulator?