single phase can run in PVC conduit. Three phase can also
run in one PVC conduit. But two phase cannot run in one PVC
conduit. WHY? reply plz....awaiting your answer.

Answer Posted / bhatt

In PVC conduit, one can run single phase, two phase and
three phase but two phases is not allowed in metalic
conduits as two phases can not cancel out magnetic field
and metalic conduit can induce voltage which can lead to
fatal accident.

Is This Answer Correct ?    11 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the saturation point of crgo lamination.

1645


What is the ratio of true power to apparent power in an ac circuit?

694


Name two types of electrical analogous for mechanical system.

740


please tell me when we start motor without load in star or delta connection whose current above condition,pl write formula

1797


What is q factor?

674






If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma

1642


what is ps impedance test

1666


why the protection turbo generators is most complex?

1513


What is the requirement of grounding the neutral of single phase generators on load? If the neutral is not grounded, what will be the effect?

1626


hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"

1617


How can I known multiplying factor .without multiplying table

1362


why ct ,cvt should be stored in a vertical position?

2132


My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?

1196


what is the formula for hv test for cable and circuit breaker..????

1546


Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?

1647