Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What is difference between earth leakage relay and
restricted earth fault relay ?

Answer Posted / p c sahu

Under normal conditions and by application of
Kirchhoff’s laws the sum of currents in both current
transformers (CTs) equals zero. If there is an earth
fault between the CTs then some current will bypass the
CT's and the sum of currents will not be zero. By
measuring this current imbalance faults between the CTs can
be easily identified and quickly cleared. Fault detection
is confined to the zone between the two CTs hence the
name 'Restricted Earth Fault'
An earth leakage relay will sense and trip the circuit for
any earth leakage fault that may occur any where in the
system. The C.T provided at the neutral bus is used for
sensing this fault

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the difference b/w pvc cu conductor and cu breaded wire..?

3556


what are factors to be consider to design a HT & LT motor?

2312


Differentiate between induced emf and self inductance?

1138


how we findout a ignater is faulty or not?

2099


WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA

2066


How a band pass filter is constructed?

1056


What are the advantages of nichols chart?

1299


What is the working mechanism of OLTC in Power Transformers????

4319


for 11KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV UG system what will be typical per KM "R" "L" "C" parameter.

2445


what is the use of Auto re-closer?

2133


I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA

3236


I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

1955


Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????

1807


What is George phenomena to start the synchronus machine?

4128


What is mean by spike arrester(Voltage Operated)

2058