Dear all,
Can anybody tell me that how to choose CT for a specific
load? I have a 200kw induction motor, which ratio CT should
be installed? Is there a formula or calculation that
determines the CT ratio for a load?
Regards.
Answer Posted / k.prakashchandra
Another method.Divide KW by 0.75 (lowest pf expected) to get
KVA. Calculate current which is about 380 A at 400 V line
voltage.You can choose a CT 0f either 400 or 500 A as
primary current.The secondary current of CT is decided by
meter and relays.This is generally either 1 or 5 A .
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
describe the phenomena of vacuum interruption in C.B
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
in an electronic tri vector meter when the current and voltage sequence changes ? what is the effect of phase sequence on recording of meter
Explain how you decide what size of electrical wire do you need?
is ac supply can store
What is meant by reset level of the relay?
control & auxilary circuits used for circuir breakers
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
what is different between relay and plc?
diff. between tension mode & speed mode
can the measured percentage error during calibration of single phase energy meter be negative?
How to design the earth grid for lightning protection in an industry
describe the Tranformer testing procedure
Where can i get practical knowledge of solar system?
What is the gross weight to copper ratio in slip ring induction motor of 4000 HP,6.6 kv, 372amp, 992 rpm GE motor.