what is the different between earth leakage relay and earth
fault relay?
Answer Posted / muhammad umair
Both Take their sensing from a ring core CT. In earth
leakage relay sensing is high i.e in mA.Where as earth fault
relay is used on higher loads where sensing is low i.e in A.
This is why earth leakage is used for the house hold devices
or power supply sockets protection. And Earth fault relay is
use for Industrial loads,motors normally more than 37KW (Not
a standard),distribution,generation etc.
| Is This Answer Correct ? | 3 Yes | 3 No |
Post New Answer View All Answers
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
HOW CAN I GET 5CORE HO7 CABLE SIZE IF I HAVE 1800A?
describe the Tranformer testing procedure
How phase displacement change in the over current relay coils.
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
where is core-type and shell-type construction suitable for transformers ?
What is the function of NGR for the parallel operation of alternator? whats happen when different rating of alternator are running with parallel?
For high frequency application we use which transformer?
I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN
What is the power factor of a transformer at no load?
What is the implications when 600 hp motor is started when the unit is running with Transformer of capacity 1500 KVA and DG set of 1000kva
What is miller crystal oscillator? Explain its operation?
i want to know about torque of slip ring induction motor
PLEASE SEND ME NTPC RELATED INFORMATION LIKE WHICH TOPICS HAV MORE SCOPE,BOOKS TO READ,CUT OFF...PLEASE.mail at thiru.1203@gmail.com
What is Primary And Secondary Injection Test of Relay and Other Electrical Devices. How IT is carried out.