what will happen to give a dc supply in ac motor?
Answer Posted / argie pineda
if you supply dc power to AC MOTOR .We all know that an ac motor is high inductance and low resistance,the motor will be burned.
Is This Answer Correct ? | 4 Yes | 2 No |
Post New Answer View All Answers
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?
How u can give the overload setting to any motor protection relay for a HT motors with formula and Example?
howmany electrician should maintain for a 1000 kva used plant... in kerala..
Name of the relay of low lub oil presuure in DG sets
how to calculate the conductor size for certain KV transmission line and distribution line?
whatis the commertial spec. of distribution boards ?
What is resistance of 50meters, 16sq.mm, single core copper cable?
How much no load current of synchronous motor
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
Why two phase welding machine is used instead of three phase welding machine.
please give me all the Alarm .Trip ,Safety Relays & Conditions of Chiller mail me on ashokbabunhce@gmail.com
what is the diff. between x'mer , isolation x'mer & ultra-isolation x'mer ?????????????
what happens to the supply voltage if there is any change in frequency?
if 3400kw slipring motor rotor shorting done and motor started on mv drive ,what will be the rotor shoring current
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end