why transformer ratings in kva?

Answer Posted / fred gleicher

KW, or kilowatt, assumes both current and voltage are in
phase. In a transformer, it is possible for current and
voltage to be out of phase ( since a transformer is
inherently normally an inductive device ). Therefore, the
rating is given in VA or volt amps, instead of watts,
showing that current and voltage may be out of phase. The K
comes from the MKS system and is an abbreviation for
thousand. It just makes it easier to write the power rating
of the device, most transformers ordinary folks see are
rated in the VA range, but electrical linemen see devices
rated in the KVA range every day.

Is This Answer Correct ?    0 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is cathodic protaction?

1497


how to design coil turns ?

1538


To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors

1534


what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?

1423


Explain difference between stand by earth fault and residual earth fault protection?

1538






why we dont prefer ac voltage controller instead dimmerstat [if both have same rating] for conducting experiments in laboratories?

1700


what is photo voltic cell,& what are the materials associated with that?and any spcifications like volts/cm etc?

1604


What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating

1034


why ct ,cvt should be stored in a vertical position?

2132


In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases

1620


How npn and pnp transistor works

645


how to calculate the power factor when instantaneous voltage and current has harmonics in it ?

1414


I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.

1675


WHAT IS THE DIFFERENCE BETWEEN AN ACB & mccb 7 WHAT IS THE CRITERIA WHEN TO USE WHICH OF THE TWO

1843


what is the meaning of impedance protected in instrument cooling fan

2802