Can We Apply DC POWER To Transformer????
And Why????
Answer Posted / ahmed
We can apply dc supply to transformer, but here impedance
is only resistance in casof DC.large amount of current will
flow through the promary windings depending on the
magnitude of primary voltage applied.Secondary will not
induce any voltage.
Is This Answer Correct ? | 4 Yes | 5 No |
Post New Answer View All Answers
why three phase capacitor takes unbalanced current in capacitor bank?
how we calculate electrical load on a building according to area?
State any two nuclear power stations in India, with their generating capacity.
What is maximum power transfer theorem?
1.how many earth pits are required for 1000 k.w plant include substion , transformer ? 2. how many earth pits are required for 500kva generator.what is formula to calcute?
what is the control circuit for operating the clean room air shower
How earthing/grounding done in aeroplanes and ships.
star delta starter contorl circuit... drawing..
HOW TO CALCULATE S/C,O/C,E/F OF ACB.
why the active power flow of some line is increased when the active power of out is cut ?
witch pump used in wtp
What is the role of power pack in substation protection system?
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
what is meant by flywheel and its role in retardation test
please tell me, how i clear the objective test? when i studied form the one book after i solved the objective ,that time i solved that qes. but if i tried solve objective form the other book then i could not solved these que.