how to calculate the current carrying capacity of a
conductor. How it is related to diameter of cable or
conductor
Answer Posted / c.rajesh
generally current carrying is depends on resistance of
conducting elements but we now pure conductors are not exists
so internal resistance is considered now calculation is made
as resistance directly proportional to area of conducting
element R=l*a/s
here l=length of conductor
a = area
s = specific conductance
Is This Answer Correct ? | 2 Yes | 15 No |
Post New Answer View All Answers
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
Explain what is electric traction?
What is capacitance?
How to design harmonic filter at the project stage without nowing the harmonics levels
What are the different types of dams?
Differentiate between ideal and non ideal current sources?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
Why 30kw 40 hp 4 pole 3ph induction motor over heated?any steps on reduction in heat?
1) Explain why we don't link the two earthing system ht and mv on a pole mounted transformer sub-station.
which connection is safer series or parallel?usually which connection we prefer at home?
What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps
fuel-air ratio in a petrol engine fitted with suction carburettor,operating with dirty air filter as compared to clean filter will be
what is dry and wet frequency withstand voltage? why & where it is used??