In hydro plant,generally we install vertical hydro
generators..why dont we recommend horizontal one??
Answer Posted / sivashanmugam
horizontal also recommended .when the dam level is too low
for eg above 60feet to 110 feet they use horizontal
generators its have capacity of 650kw
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
what is the criterion for selecting vector group of Transformers ? i mean how to decide vector group of Generator transformer, substation trasformer and transformer at consumer end
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
Is it good to short Neutral and Ground in the PLC or DCS main Power supply. Pls give YES or NO with reasons...? Simarpreet
what is metering cum synchronizing panel and how it is used?
What is the loss of power of transformer 220kv/33kv,63/80mva of % imp12.05 at 80%load
how does the rotating m.m.f is produced in the 3-phase induction motor and how the poles are created in 3-phase induction motor ?
what is the Earth Voltages in Power Plants, Sub-stations, Industries, Residential & Commercial Buildings.
can i connect REF and Differencial relay in 1 CT core for transformer protection?
when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??
Hi,iam a diploma in electrical engineering.rtd from indian air force in apr 2007.prsently working in reliance next link as a network maintenance engineer since 2007,can i get a job in motherson sumi.
how the inner and outer body is separated in aircrafts?
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
what is the cause of voltage dipp or swell in the transmission lines?
What is the emf equation of a transformer?
what is mean by dry frequency