Caliculate the Specific Fuel consumption of 320 kva diesel
genarator set?
Answer Posted / sriram.b
We have to measure the fuel consumption per one hour of the required DG. Simultaneously check the generated units from kWh meter at approx.80% load. Divide Units with consumed diesel.
We will get the specific fuel consumption of DG.
| Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
how did the testing of protection relays done through current injection
what is the power rating of CPU, CRT type moniter, LCD type moniter,scanner Approx.
we need a ntpc previous papers
what could be the RMS value and average value of a 4 phase sine wave?
whether fibre optic cable in high voltage earth conductor is used for protection circuits
diff.between servo motor and ac motor
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
we are having 15kw and 3kw motor both can run in same time , instead of using copper we are using ug aluminium cable , 35 sq.mm is suitable for its current carrying capacity..?
what happen when we add mentos in cold drink?& why?
Explain M Var? Which types of problem occurs when reactive power increase at the time of full load of plant and at the time of synchronize of plant?
when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??
when the Transmission and Distribution network where is the "feeder" lines are located? and why should be used in T&D network.....
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
I am having a 1500 KVA transformer whose secondary current is 2086A and my connected load is 1000 KVA, I am having 400 KVAR APFCR for PF improvement what ratio of CT should i install in LT EB Bus to get optimum PF improvement?
what is the minimum winding resistance of 30hp compressor, to run or to switch on