What is difference between earth leakage relay and
restricted earth fault relay ?
Answer Posted / rv
ref- this protection is designed to look back towards the
secondary windings of the suppl transformer and all small
control wiring and other current transformer.
while earth leakage relay is designed to protect the
circuit in the unit.
| Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
what is the difference b/w pvc cu conductor and cu breaded wire..?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
solor panels arrange some angle,panel is flat fitted energy was produced or not why?
what is the effect of change in supply frequency on load angle of synchronous motor,all other parameters remaining same?
How generating electric power export to grid from the generating station ?
why we cannot protect 100% winding of an alternator by using differential protection?
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
What types of CMOS memories have you designed? What were their size? Speed? Configuration Process technology?
i have completed deee and i've (June2012-feb 2015 experience in electrical maintenance in pvt ltd company.company having HT & LT electrical power.how to apply electrical C-license ,NOW I was resigned my job,what are requirements of applying for c-license
in dc shunt motor if field winding is shorted then
what is the minimum winding resistance of 30hp compressor, to run or to switch on
what is circuit breaker in transfomer and where it used
What are the transformer losses?
How to checked frequency drive output voltages?