1> what r different types of fault in cables? How will u
locate and test these faults?
2> why earth wire is provided on top throughout the
transmission line. why not only on towers? How much area it
can protect?
3> what r different types of transmission losses? How power
loss can be minimized?
4> what is the % of power loss on transmission lines?
Answer Posted / rahul maddineni
1)The most frequent fault in under ground cables is Short
circuit(phase to phase)due to insulation layer gets heated
and burst.It can be tested by using Megger and fault
locatoin can be detected by Cable Detector.
2)Earth wire will protect the conductors from Lightening
surges and it provide the low resistance path for the over
currents during lightening.
3)Transmission losses are a)I^2R losses b)Corona losses.
4)May be 5% to 10% and also depends up on the type of alloy
of material
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
Z transform is use when system is not a) converges b) diverges
would the same effect be achieved by reversing the connection to one winding of the induction motor 3-phase?
what are the analog quality input for protection function?what are minimum reqiments?
can anyone explain 11kV 3core cable megger,hi pot test procedure with connection details?
What is an automatic controller?
I want d.g.set our company
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
what is active power & reactive power?
Distinguish between nuclear power station with thermal power station for initial cost, starting period, cleanliness, and transportation of fuel
why genarator genarating voltage 11 KV?
what is the function of anti pumping relays? what is KVAR? How it is generated in alternator? What is 3rd Harmonics? What is IDMT relay?
can i use 4 number of circuit breaker as single phase manual change over switch? if yes then how plz also send ckt diagram at nazimzamurad@gmail.com
What is the most accurate way of testing ELCB?ELCB is better than RCD?
Any one who apply for Ferro Scrap Nigam Limited cn join with me at rajuhalder@indiatimes.com or 09669717028
what is the difference between gas group b and gas group c electrical equipment construction wise?