What is transformer tap changers please explain
Answer Posted / bharani
Transformers in general can have tappings in both primary
and secondary.
When we talk of HT transformers, tappings are provided in
the primary winding, this helps us in getting proper output
voltage by changing the tapping whenever the HT voltage
varies from the actual specified voltage.
| Is This Answer Correct ? | 9 Yes | 1 No |
Post New Answer View All Answers
WHAT ARE THE DATAS REQUIRED FOR PROTECTION AND METERING AND CONTROL AND LOGIC PREPARATION,HOW TO STUDY THE PROTECTION AND METERING?
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
whate is the meaning of balance/unbalance,in stabilizers type
is it true there's a big difference in using Cummins or Denyo...especially power output or leakage
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
What is a surge supressor why its is used in synchronous generators
armature is that part in which current is induced since in dc motor we supply current to the conductor so why we call it armature?
what is the eight bit unit?
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
How we can calculate the Amps for the cable Ex:- For 1sqmm wire how many amps we can draw (calculation)
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
can any tell me why slope 40% and 80% is calculated in differential protection?
How 3 phase invertor works?
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
WANTCONTACT NUMBER & EMAIL/ WEBSITE TO CONTACT THE SECRETARY,MADHYA PRADESH LICENSING BOARD(ELECTRICAL),K- BLOCK,3RD FLOOR,SATPOODA BHAWAN,BHOPAL