What is mean by Sensitive Earth fault & what are the effects
Answer Posted / khrabsheh
Sensitive Earth Fault Protection Normally used on systems where the earth fault current is limited to a very low value (Neutral earthed through resistors, Peterson coil, reactance, etc) Scheme consists out of a ring CT (Core Balance CT) around the three phase conductors, and the relay connected to the secondary side of the CT. A very low setting is possible, even sometimes lower then 1% FLA. Need to coordinate with similar relays downstream.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
which type of amplifiers are used in multimete?
what is the problem when i want to close a circuit breaker by local position it closes well.but when i close it in remote position it trips
State the types of distortions in amplifier?
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
Can any one provide the inspection procedure of MIMIC for VFD panel? Details: If someone wants to have a mimic in the VFD panel what are inputs considered for the mimic(like on,off,trip) whether we are able to add speed variation in the mimic(if so how can we get) and what are the parameters to be checked in the MIMIC during inspection?
HOW MUCH CURRENT DOES SYNCHRONOUS MOTOR TAKES AT SYNCHRONOUS SPEED IN NO LOAD CONDITION ?
In a flange coupling, the flange bolts are designed for
Starting current of a 10 HP induction Motor is ______ time’s full load current.
What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance
whate is the meaning of balance/unbalance,in stabilizers type
hello friends..... any one have papers or any study materials?sail ,hpcl...?
what curve and rateing would you use for a three phase 0.75kw motor?
i want to know that how the height of Ct ,cvt ,LA calculated on the basis of creepage distance
what is the formula for calculating the phase clerance between two phases and phase to earth how to calculate the cable for a motor
what is vA rating and class of a ct.